I don't know anything about electrical stuff.

I was rearranging my house, and I plugged in a power strip. Apparently this strip has some kind of alarm built into it, and the thing started going off. I tested the strip in three different outlets (each in a different room), and only one of them didn't set off the alarm (the one it had until now been plugged into).

I got out my multimeter... first time I've ever used one. The outlet that didn't trip the alarm reads about 105V or 110V. The other two I tested read about 100V or 105V. I can't read the faint little lines very precisely, but they were all conspicuously under 120V, and one was conspicuously higher than the other two.

Is this a big deal? Should I call my landlord? Should I refrain from plugging my gear into these outlest?

What's the deal?
_________________
Love your new bananaskin shoulderpad,
Cody C. Gaisser
www.myspace.com/codygaisser
Back to top
View user's profile Send private message Visit poster's website AIM Address Yahoo Messenger
Gregg Juke
resurrected


Joined: 12 Jun 2010
Posts: 2280
Location: Buffalo, NY, USA

PostPosted: Sat Jan 07, 2012 3:12 am    Post subject: Re: Newb: Wall outlet issues (power strip alarm, meter: 100V) Reply with quote

I don't think it's a big deal (said the totally unknowledgeable about electric guy). But, you could try to up the ante as far as steady power by using a Furman power regulator or a UPS with regulation, or both.

We have a UPS with regulation in the control room, and a Furman conditioner in the studio tracking room. We also have a regulator for live use with the band. They do work, but you never really get _perfect_ on-the-money 110; it fluctuates between something like 105 - 120, but it does keep things within that range. And, if you do get any kind of spike, you will at least have constant metering to see it coming. If you get a regulator, it locks things down within that range, protecting against spikes and brownouts. If you get a UPS, you will have some added protection for your delicate electronics in case you ever lose power completely.

Not cheap, but kind of a necessary expense, I suppose.

GJ
Back to top
View user's profile Send private message Visit poster's website
RodC
dead but not forgotten


Joined: 31 Dec 2004
Posts: 2036
Location: Right outside the door

PostPosted: Sat Jan 07, 2012 9:12 am    Post subject: Re: Newb: Wall outlet issues (power strip alarm, meter: 100V) Reply with quote

I would measure the voltage with all your stuff plugged in. You may have a real long run to that outlet, undersized wire, or a bad connection. I would meter it at the breaker box, then at the outlet and see how much it dropped.

IF you know everything that is on the circuit you can unplug everything, read the voltage, (this will = your source voltage) then plug everything in, fire it up, then take a reading. The difference will be the drop.

<ramble>With no load you will read the source voltage, (ohms law) same reason the voltage across a blown fuse will read source voltage. (Best way to check a fuse, I have seen several that break down under a load) </ramble>


If you feel anything getting hot, if there is a huge voltage drop you may have a bad connection, not safe.
_________________
'Well, I've been to one world fair, a picnic, and a rodeo, and that's the stupidest thing I ever heard come over a set of earphones'

http://www.beyondsanityproductions.com
http://www.myspace.com/beyondsanity
Back to top
View user's profile Send private message Send e-mail Visit poster's website
AnalogousGumdropDecoder
pushin' record


Joined: 10 Apr 2008
Posts: 219
Location: Nashville, TN

PostPosted: Sun Jan 08, 2012 9:33 pm    Post subject: Re: Newb: Wall outlet issues (power strip alarm, meter: 100V) Reply with quote

I appreciate the response, but I don't have any idea how to check that kind of stuff. I just rent an old house and recently moved gear from one room to another and had that alarm go off. I just kind of don't know whether I can turn my gear on without calling an electrician.
_________________
Love your new bananaskin shoulderpad,
Cody C. Gaisser
www.myspace.com/codygaisser
Back to top
View user's profile Send private message Visit poster's website AIM Address Yahoo Messenger
goose134
takin' a dinner break


Joined: 22 Mar 2009
Posts: 194

PostPosted: Mon Jan 09, 2012 12:07 am    Post subject: Re: Newb: Wall outlet issues (power strip alarm, meter: 100V) Reply with quote

Take a power strip, plug the equipment into it, leaving at least one space open. Run the equipment and take a voltage reading at the empty space in the power strip. One thing that comes to mind is a neutral problem. Open or loose neutrals will manifest themselves under load. They can usually be diagnosed with rambling voltage or current under load.
100 to 105 does sound pretty low. While it is possible that a long run is causing it, That is a significant drop for an average house. Typically wire won't be upsized until you start getting 80 or 100 feet from the panel.
If you find that the voltage readings wander depending on the load imposed, tell your landlord you have a problem with it. If you need backup, I'd be happy to educate him on the dangers of an open neutral in a multi-wire branch circuit. It's usually a matter of tightening loose connections. Sometimes, it's on the service side, but since you say there is one outlet that works, it may not be that,
Until you figure out what is causing it, refrain from plugging computers or vintage amps into the offending outlets. What basically happens in an open neutral in a multi-wire branch circuit is that the circuit turns to a 240 volt ciircuit, blowing anything you've got on it.

Sorry for the long post. While I learn much in the way of sound on this forum, electricity is one area I have much to teach.
_________________
I make a living as an electrician, not recording in the basement.
Back to top
View user's profile Send private message
AnalogousGumdropDecoder
pushin' record


Joined: 10 Apr 2008
Posts: 219
Location: Nashville, TN

PostPosted: Mon Jan 09, 2012 1:54 am    Post subject: Re: Newb: Wall outlet issues (power strip alarm, meter: 100V) Reply with quote

I did that test while running a CD player, stereo, turntable, phono preamp, and another power amp. The meter read about 105.
_________________
Love your new bananaskin shoulderpad,
Cody C. Gaisser
www.myspace.com/codygaisser
Back to top
View user's profile Send private message Visit poster's website AIM Address Yahoo Messenger
Brian
dead but not forgotten


Joined: 02 Jun 2003
Posts: 2222
Location: corner of your eye

PostPosted: Mon Jan 09, 2012 8:29 am    Post subject: Re: Newb: Wall outlet issues (power strip alarm, meter: 100V) Reply with quote

You probably have a bad connection at the main breaker box. It's common with older housing and sometimes newer that the screws didn't get tightened properly on the grounding post in the box, also, a lot of the houses I've renovated had bad connections at he outlets too, so they may need tightening too.

Sometimes the hot leg is loose in the breaker switches.

Is your electric bill high for what you have running?

If you have loose connections, when the voltage drops, some equipment will try to make up for it by sucking in amperage! That causes excessive heat and can damage equipment, it can also cause heat in the outlets and start a FIRE.

DANGEROUS!

TURN THE POWER TO THE WHOLE BOX OFF BEFORE TIGHTENING SCREWS.

I just replaced a fusebox in my latest house and when I turned on the power, fridge is quieter, lights are brighter, the kids noticed as soon as they came home without knowing I did any work, and everything works better, and in Memphis, the electricity is extremely unreliable voltage wise, constant overvoltage condition to 126 127 volts with voltage and power spikes.
It will Fry your stuff.

and just to verify the above posters post, there were completely lifted grounds in the fusebox causing all the problems. Problem solved here.
_________________
Oh shut up.
Back to top
View user's profile Send private message Send e-mail Visit poster's website
goose134
takin' a dinner break


Joined: 22 Mar 2009
Posts: 194

PostPosted: Tue Jan 10, 2012 12:00 am    Post subject: Re: Newb: Wall outlet issues (power strip alarm, meter: 100V) Reply with quote

AnalogousGumdropDecoder wrote:
I did that test while running a CD player, stereo, turntable, phono preamp, and another power amp. The meter read about 105.


OK, So what does it read when there is no load? If it's much higher, than start poking around for loose connections. PLEASE! If you go in the panel, kill the power. If there are aluminum conductors as opposed to copper, there are likely to be loose ones. This is especially true if it's an older service.

Actually, another thing you could do is measure voltage on the other tenant's outlets and then a neighbor's outlet. Maybe an outside outlet so you wouldn't look like a complete weirdo. I'm just trying to see if 105 is your baseline on a wider scope. It seems low. In my area 125 isn't uncommon, but it's usually 121.
_________________
I make a living as an electrician, not recording in the basement.
Back to top
View user's profile Send private message
standup
buyin' gear


Joined: 01 Nov 2004
Posts: 518
Location: Baltimore

PostPosted: Tue Jan 10, 2012 12:52 am    Post subject: Re: Newb: Wall outlet issues (power strip alarm, meter: 100V) Reply with quote

Sorry to hijack, but I've got a nagging question. All my recording gear runs off a Furman power strip with an LED showing voltage. If I walk into the room with everything powered down, it will probably read 120v solidly. As I turn on the computer, monitors, racks, it starts flickering a couple times a second between 118v and 120v.

No big deal, or should I think about what that means?
Back to top
View user's profile Send private message Visit poster's website
AnalogousGumdropDecoder
pushin' record


Joined: 10 Apr 2008
Posts: 219
Location: Nashville, TN

PostPosted: Tue Jan 10, 2012 2:52 am    Post subject: Re: Newb: Wall outlet issues (power strip alarm, meter: 100V) Reply with quote

Consistently reading about 105 at most jacks. Haven't tested every single one because they're not very accessible, but I've tested one in each room. One reads about 110, which apparently is just enough not to make my power strip scream at me.
_________________
Love your new bananaskin shoulderpad,
Cody C. Gaisser
www.myspace.com/codygaisser
Back to top
View user's profile Send private message Visit poster's website AIM Address Yahoo Messenger
Snarl 12/8
moves faders with mind


Joined: 20 Dec 2008
Posts: 2709
Location: Portland

PostPosted: Tue Jan 10, 2012 3:38 am    Post subject: Re: Newb: Wall outlet issues (power strip alarm, meter: 100V) Reply with quote

In my opinion brown outs (low voltage) is very dangerous to equipment. Anything with a motor (fans, drives, tape decks) would probably rather be slightly over powered than under. That's something I learned a long time ago that's proven to be true over the years. Also, I think it's easier for gear to be protected against an over (simple fuse) than against under powered, so that becomes an equipment operator's headache. I'd track that fucker down.
_________________
Carl Keil
Back to top
View user's profile Send private message Visit poster's website
Brian
dead but not forgotten


Joined: 02 Jun 2003
Posts: 2222
Location: corner of your eye

PostPosted: Tue Jan 10, 2012 9:11 am    Post subject: Re: Newb: Wall outlet issues (power strip alarm, meter: 100V) Reply with quote

AnalogousGumdropDecoder wrote:
Consistently reading about 105 at most jacks. Haven't tested every single one because they're not very accessible, but I've tested one in each room. One reads about 110, which apparently is just enough not to make my power strip scream at me.


Straight up:
It's not enough voltage, GET IT FIXED. ASAP, it could cause a FIRE.
Got it?
_________________
Oh shut up.
Back to top
View user's profile Send private message Send e-mail Visit poster's website
goose134
takin' a dinner break


Joined: 22 Mar 2009
Posts: 194

PostPosted: Tue Jan 10, 2012 11:18 pm    Post subject: Re: Newb: Wall outlet issues (power strip alarm, meter: 100V) Reply with quote

AnalogousGumdropDecoder wrote:
Consistently reading about 105 at most jacks. Haven't tested every single one because they're not very accessible, but I've tested one in each room. One reads about 110, which apparently is just enough not to make my power strip scream at me.


Ok. If it's reading that low throughout the place, then it's probably at the service. This is where I recommend you mention the problem to your landlord, softening the blow by telling him that it is more than likely a simple fix. I say more than likely, but as with many hacked together DIY jobs, drywall conceals a multitude of sins.
Here are my working theories at this point with suggestions on remedies:
1. Loose Nuetral (or hot) connection at the panel.
Have the electrician check the tightness of the incoming service entrance conductors (wires under main breaker) and the branch circuits.
2. Loose connection in meter
Same advice as above
3. Improper or absent neutral bond
As I recall, yours is a multi unit and you didn't say how larger, but there should be only ONE neutral to ground connection made at the service. If it's a small building, there may be 2 or 3 panels fed from the same service. The neutral should be bonded to the enclosure in one of the panels. Have your electrician confirm it is present and properly sized and terminated.
4 Water ground (grounding electrode conductor)
While it doesn't have anything to do with wandering voltage, as long as he's there, make sure your panel is grounded to the water main properly.
5. Utility transformer undervoltage (this is only if your neighbors are suffering the same problem)
If the electrician finds everything in order then it may be a POCO problem (POwer COmpany) Before calling, confirm your neighbors are sharing this problem.
Now all this sounds daunting, but understand that all of the work I've described should be in a small area and shouldn't necessitate punching holes in the wall or anything. This should be a 2 hour service call. As has been mentioned, undervoltage will do more damage to equipment than slightly higher voltage. Have him (or her) call someone reputable. Confirm that the problem is at the panel. If it is, the mains should read 105 volts as well. Keep me posted. Sorry again about the long post. That electricity, she's more complicated than you think!
_________________
I make a living as an electrician, not recording in the basement.
Back to top
View user's profile Send private message
goose134
takin' a dinner break


Joined: 22 Mar 2009
Posts: 194

PostPosted: Tue Jan 10, 2012 11:21 pm    Post subject: Re: Newb: Wall outlet issues (power strip alarm, meter: 100V) Reply with quote

standup wrote:
Sorry to hijack, but I've got a nagging question. All my recording gear runs off a Furman power strip with an LED showing voltage. If I walk into the room with everything powered down, it will probably read 120v solidly. As I turn on the computer, monitors, racks, it starts flickering a couple times a second between 118v and 120v.

No big deal, or should I think about what that means?


Not a problem. 105 volts? Problem.
Maybe a piece of electrical tape over the offending meter will help Wink
_________________
I make a living as an electrician, not recording in the basement.
Back to top
View user's profile Send private message
Galen Ulrich Elfert
gettin' sounds


Joined: 06 Nov 2007
Posts: 121

PostPosted: Tue Jan 24, 2012 3:49 pm    Post subject: Re: Newb: Wall outlet issues (power strip alarm, meter: 100V) Reply with quote

This is probably not the issue, since you've got that alarm going, but for the benefit of the thread: I scared the bejeezus out of myself a little while back when I happened to measure my mains at 160v. Turned out the battery in my cheap multimeter was dying.
Back to top
View user's profile Send private message
Display posts from previous:   
Post new topic   Reply to topic   printer-friendly view    Tape Op Message Board Forum Index -> Making A Space All times are GMT - 4 Hours
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum